Thread: Looking for electrical help---GFCI outlet tripped in kitchen

  1. #11
    Site Supporter EricM's Avatar
    Join Date
    Jan 2012
    Location
    Midwest
    Quote Originally Posted by peterb View Post
    Don't forget kitchen or wet bar areas. Per 210.8(A)(6), GFCI protection is required for all 15A and 20A, 125V receptacles that serve kitchen countertop surfaces in a dwelling unit (Fig. 1 on page 54). GFCI protection is not required for receptacles serving appliances like dishwashers, or convenience receptacles that do not supply countertop surfaces. Receptacles installed within 6 ft of the outside edge of a wet bar sink must also be GFCI-protected [210.8(A)(7)]. However, GFCI protection is not required for receptacles not intended to serve wet bar countertop surfaces, such as refrigerators, ice makers, water heaters, or convenience receptacles that do not supply counter-top surfaces.

    https://www.ecmweb.com/national-elec...errupters-gfci
    I believe that article is outdated (2002); my understanding is current code (starting with 2014) requires GFCI protection for dishwashers.

    As farscott indicated, other outlets connected to the Load side of a GFCI outlet are protected by the GFCI and thus issues there could cause it to trip. It might narrow things down to leave the other outlets disconnected and see if the problem persists.

  2. #12
    Member Baldanders's Avatar
    Join Date
    Jul 2017
    Location
    Rural North Central NC
    Quote Originally Posted by EricM View Post
    I believe that article is outdated (2002); my understanding is current code (starting with 2014) requires GFCI protection for dishwashers.

    As farscott indicated, other outlets connected to the Load side of a GFCI outlet are protected by the GFCI and thus issues there could cause it to trip. It might narrow things down to leave the other outlets disconnected and see if the problem persists.
    I went under the house and I think I identified the power cord that runs to the dishwasher. I couldn't see any damage.

    I am thinking about capping off all the outlets on the same circuit (all are within 6ft of the sink) if I can't find the issue otherwise. We really just need the dishwasher and the light above the sink.
    REPETITION CREATES BELIEF
    REPETITION BUILDS THE SEPARATE WORLDS WE LIVE AND DIE IN
    NO EXCEPTIONS

  3. #13
    Gucci gear, Walmart skill Darth_Uno's Avatar
    Join Date
    Aug 2017
    Location
    STL
    If there's no additional outlets on the circuit, you can bypass the GFCI. Simply put all wires into the "line" terminals. This will allow the GFCI to function correctly where it's installed, but doesn't protect anything downstream. Which should be fine if the only item is the dishwasher - anything motor-driven should be on its own circuit, or at the very least not GFCI protected.

    If you do have additional outlets on the circuit, and they're within 60" of the sink, you may just want to pay an electrician to come out and make sure everything is kosher. Local code says any outlet (not hard-wired appliance) within 60" of a water source (sink/faucet) must be GFCI protected, which I would strongly recommend sticking with that.

  4. #14
    Member Baldanders's Avatar
    Join Date
    Jul 2017
    Location
    Rural North Central NC
    Quote Originally Posted by Darth_Uno View Post
    If there's no additional outlets on the circuit, you can bypass the GFCI. Simply put all wires into the "line" terminals. This will allow the GFCI to function correctly where it's installed, but doesn't protect anything downstream. Which should be fine if the only item is the dishwasher - anything motor-driven should be on its own circuit, or at the very least not GFCI protected.

    If you do have additional outlets on the circuit, and they're within 60" of the sink, you may just want to pay an electrician to come out and make sure everything is kosher. Local code says any outlet (not hard-wired appliance) within 60" of a water source (sink/faucet) must be GFCI protected, which I would strongly recommend sticking with that.
    Thanks buddy. There are 2 regular outlets "downstream," so I think eventually I will do as you suggested, then replace the downstream outlets with GFCI models as well.

    But for now I'm capping off the first outlet and putting childproof plugs in the others. I have a lot of school shit I need to attend to, especially due the internet outage of the past few days.
    REPETITION CREATES BELIEF
    REPETITION BUILDS THE SEPARATE WORLDS WE LIVE AND DIE IN
    NO EXCEPTIONS

  5. #15
    Member Wheeler's Avatar
    Join Date
    Mar 2011
    Location
    Jawja
    Newer code requires GFCI protection on dishwasher outlets, that's regardless of whether there is an actual cord and plug assembly or it's hard wired. Typically the correct course of action is to run a dedicated, 20A circuit and install on a GFCI breaker. The newer dishwashers have different failure points than the older, electro mechanical styles.

    Any outlet with 6' of a water source, such as a sink require GFCI protection. Code also requires an outlet every 2' of counter space and no more than two outlets per circuit. Obviously that's not the case with your situation. Bypassing the GFCI protection is not necessarily the best course of action. It's also prudent to note that if your dishwasher is tripping the new GFCI that can be indicative of an issue with the actual dishwasher and not the electrical system.

    Do you have more than one GFCI outlet on that circuit? If so that will create all sorts of issues.

    If you'd like, shoot me a PM and we can swap numbers, I might be able to talk you through troubleshooting.
    Men freely believe that which they desire.
    Julius Caesar

  6. #16
    Member Baldanders's Avatar
    Join Date
    Jul 2017
    Location
    Rural North Central NC
    Quote Originally Posted by Wheeler View Post
    Newer code requires GFCI protection on dishwasher outlets, that's regardless of whether there is an actual cord and plug assembly or it's hard wired. Typically the correct course of action is to run a dedicated, 20A circuit and install on a GFCI breaker. The newer dishwashers have different failure points than the older, electro mechanical styles.

    Any outlet with 6' of a water source, such as a sink require GFCI protection. Code also requires an outlet every 2' of counter space and no more than two outlets per circuit. Obviously that's not the case with your situation. Bypassing the GFCI protection is not necessarily the best course of action. It's also prudent to note that if your dishwasher is tripping the new GFCI that can be indicative of an issue with the actual dishwasher and not the electrical system.

    Do you have more than one GFCI outlet on that circuit? If so that will create all sorts of issues.

    If you'd like, shoot me a PM and we can swap numbers, I might be able to talk you through troubleshooting.
    Quite a bit of the wiring in this house ain't up to code. Put together by a Chapel Hill cop with family help, not sure how it passed the inspection during the purchase process. When we sell, we are going to have to spend a good chunk of change to get everything right.

    There is only one GFCI outlet on that circuit--but two outlets downstream The washer is 1 month old, and it's own sensors tripped when it detected water underneath --had a leakage problem when I initially installed it, now corrected.

    The house was built in 2002, but I'm pretty sure the way the DW is wired into a circuit with a bunch of outlets wasn't code at the time either.

    After thinking about it, I think my medium term fix will be to cap off all outlets on the circuit aside from what I assume is the last one in the series, and replace that one with a GFCI outlet.

    My theory is there is a "current leak" somewhere in the line running through the gap between wall and floor, but judging by what I saw under the house, replacing that is going to be a megabitch, and probably getting into my Dunning Kruger danger zone for wiring.

    Thanks for the offer, I may take you up on it in the near future!
    REPETITION CREATES BELIEF
    REPETITION BUILDS THE SEPARATE WORLDS WE LIVE AND DIE IN
    NO EXCEPTIONS

  7. #17
    Member Baldanders's Avatar
    Join Date
    Jul 2017
    Location
    Rural North Central NC
    I've mentioned it before on PF, but I have to say I still am stunned when I think about my tech crew for theater lighting in high school experience where I was allowed to mess around with 440v wiring with no adult supervision from ages 14-16. Almost got killed cutting into a live line due to a mistake by a guy who was allowed to run the crew after me.

    Dumb. Puttering around the house now is bad enough.
    REPETITION CREATES BELIEF
    REPETITION BUILDS THE SEPARATE WORLDS WE LIVE AND DIE IN
    NO EXCEPTIONS

  8. #18
    Hokey / Ancient JAD's Avatar
    Join Date
    Jul 2011
    Location
    Kansas City
    It’s just AC.
    Ignore Alien Orders

  9. #19
    If I am understanding this correctly you have a GFCI followed by a switch/receptacle combo, two outlets and then a third outlet feeding the dishwasher?
    I wouldnt move the GFCI from where its at. You could place it after the problem which may not be enough to trip the breaker.
    I would pull the GFCI, just pull it out of the box no need to unwire yet (kill the breaker and verify no voltage present with a meter) and determine if there is one or two romex cables leaving the GFCI box. (One feed from circuit breaker entering the box so that would be a total of three cables)
    I think you need to determine where the DW is being fed from and take it out of the circuit at that point
    If there is two cables leaving determine with continuity meter which one goes to the DW.
    If there is only one cable leaving then pull the other receptacles until you find the DW feed.
    Disconnect the DW feed and see if the GFCI holds.
    If it does hold then unplug the DW and reconnect the DW circuit. If it holds then the problem is in the DW.

    Dont get locked in on the DW just yet. The problem could be anywhere in the circuit. The tripping could just be coincidental.

    Ill also offer a phone call if you need some advice just PM me.
    Last edited by UNK; 08-08-2020 at 11:25 PM.
    I'll wager you a PF dollar™ 😎